<FONT FACE="Times, Times New Roman"><SPAN STYLE='font-size:12.0px'>I want to thank you all for your input. &nbsp;I&#8217;d like to clarify something and verify if my take is correct or not.<BR>
<BR>
The situation, as a reminder, is that a completed, multi-story Time Share building, with a conditioned interior corridor on each floor, was modified to pressurize the building, both corridor and units. &nbsp;The design revisions implemented were to pressurize the corridor and undercut the unit doors to thereby pressurize the units as well.<BR>
<BR>
NFPA 80 allows up to a 3/4&#8221; undercut. &nbsp;Fine. &nbsp;But, my take is that the door&#8217;s integrity and therefore its rating, have been compromised by making field cuts to create the 3/4&#8221; undercut. &nbsp;We&#8217;re talking 45-minute HM doors, Yes or No?<BR>
<BR>
Also, FBC mechanical code....<BR>
</SPAN></FONT><SPAN STYLE='font-size:12.0px'><FONT FACE="Courier New"><B>601.2 Air movement in egress elements.</B> Corridors shall not serve as supply, return, exhaust, relief or ventilation air ducts. <BR>
</FONT><FONT FACE="Times, Times New Roman"><B><BR>
</B></FONT><B><FONT FACE="Courier New">Exceptions:</FONT></B><FONT FACE="Courier New"> &nbsp;<BR>
<BR>
</FONT><FONT FACE="Times, Times New Roman"> </FONT><FONT FACE="Courier New">1. Use of a corridor as a source of makeup &nbsp;air for exhaust systems in rooms that open directly onto such corridors, &nbsp;including toilet rooms, bathrooms, dressing rooms, smoking lounges and janitor &nbsp;closets, shall be permitted, provided that each such corridor is directly &nbsp;supplied with outdoor air at a rate greater than the rate of makeup air taken &nbsp;from the corridor.</FONT><FONT FACE="Times, Times New Roman"> &nbsp;<BR>
</FONT><FONT FACE="Courier New">2. Where located within a dwelling unit, the use &nbsp;of corridors for conveying return air shall not be prohibited.</FONT><FONT FACE="Times, Times New Roman"> &nbsp;<BR>
</FONT><FONT FACE="Courier New">3. Where located within tenant spaces of &nbsp;1,000 square feet (93 m2) or less in area, utilization of corridors &nbsp;for conveying return air is permitted.</FONT><FONT FACE="Times, Times New Roman"> <BR>
<BR>
My take on Exception #1 is that this would not permit the residential unit from opening directly onto a corridor for all this pressurized makeup air. &nbsp;The only component of the unit that has exhaust systems that would require make up air are the bathrooms and washer/dryer closet, neither of which opens directly to the corridor as the code states. &nbsp;Yes or No?<BR>
<BR>
Since this is a common corridor, and means of egress, I don&#8217;t see either Exception #2 or #3 applying. &nbsp;Yes or No?<BR>
<BR>
At some point I need to submit this information to the Building Official stating my concerns and exceptions to this solution having been approved. &nbsp;I just want to confirm my understanding of the code.<BR>
<BR>
Thank you.<BR>
<BR>
Eric<BR>